i m working on an old machine that has a layout of
1 cpu 6es7 315-6tg10-0ab0 (bus adresss 2)
1 et200s 6es7 151-1aa04-0abo (bus adress 4)
1 et200s 6es7 151-1aa04-0abo (bus adress 5)
1 et200s 6es7 151-1aa04-0abo (bus adress 6)
1 10'' OP mp277 (bus adress 7)
1 servo drive korlmorgen servostar 600 (bus adress 10)
1 servo drive korlmorgen servostar 600 (bus adress 12)
1 of the et200s panels( adress 5) was damaged during transfer. some of the modules casings were broken/cracked, so i changed all the modules(et200s, 3x pme-24vdc, 8x 4DI and and 6x 4DO) to be sure.
when i turn the power on CPU led status is,
DC 5V ON
RUN ON
SF ON
BF1 BLINKING.
i can connect and upload program from the plc but i cant get online, says online communication can not be established. thats my 1st problem.
2 of the et200s modules and mp277 communicating( i can see relative inputs and outputs turning on/off from touch panel) i havent checked the servo drives. but the one et200s module(adress 5) that i changed is in error status.
SF is on BF is blinking.
also the pme 24v dc is in error status( pwr is on sf is on)
i did try every module on that setup including et200s induvidually on a working station and they are all working. the bus adress switches are correct.
since i cant get online with the cpu, i cant run diagnostics and i have no idea where to start looking. i dont know is 1 error triggering some more or they are individual/unrelated errors.
if anyone can point me some direction, that would be much appreciated.
1 cpu 6es7 315-6tg10-0ab0 (bus adresss 2)
1 et200s 6es7 151-1aa04-0abo (bus adress 4)
1 et200s 6es7 151-1aa04-0abo (bus adress 5)
1 et200s 6es7 151-1aa04-0abo (bus adress 6)
1 10'' OP mp277 (bus adress 7)
1 servo drive korlmorgen servostar 600 (bus adress 10)
1 servo drive korlmorgen servostar 600 (bus adress 12)
1 of the et200s panels( adress 5) was damaged during transfer. some of the modules casings were broken/cracked, so i changed all the modules(et200s, 3x pme-24vdc, 8x 4DI and and 6x 4DO) to be sure.
when i turn the power on CPU led status is,
DC 5V ON
RUN ON
SF ON
BF1 BLINKING.
i can connect and upload program from the plc but i cant get online, says online communication can not be established. thats my 1st problem.
2 of the et200s modules and mp277 communicating( i can see relative inputs and outputs turning on/off from touch panel) i havent checked the servo drives. but the one et200s module(adress 5) that i changed is in error status.
SF is on BF is blinking.
also the pme 24v dc is in error status( pwr is on sf is on)
i did try every module on that setup including et200s induvidually on a working station and they are all working. the bus adress switches are correct.
since i cant get online with the cpu, i cant run diagnostics and i have no idea where to start looking. i dont know is 1 error triggering some more or they are individual/unrelated errors.
if anyone can point me some direction, that would be much appreciated.