S7-300 Profbus Problem
alijuda
Jan 2013
Iraq
62
Dear Friends
I have S7-315 2DP profbus network and I have problem to start up this network because the main PlC couldnt communicate with all Nods I have 4 Node addressed with
ET200 S (IM151-1 Standard ) with address : 1
===========================================: 3
===========================================: 4
===========================================: 5
Only Nods : 1,4 working normally and the another nods not active
Please and advice for this problem
Best Wishes and many thanks for help
rregards
Ali
I only see two configured slaves in your hardware configuration.
Slave with address 1 seems ok, slave with address 4 is not available or has an error.
You have to configure the other devices in your hardware configuration.
Dear Thomas
Thanks for reply
Yes Your Point is correct , But I try with two nods only and also this not succssed
also I checked the HW config for Node -4- its correct
I dont know is the distance between nods can caused this problem
the distance around 300M and the network speed 1.5MB
The Profibus manuals say, at 1500 kbit/s a maximum length of 200 meter, at 500 kbit/s a maximum length of 400 meter. I would go down to 500 kbit/s.
Important is the correct bus termination. Have you checked this?
In such cases I go around with my programming device, connect it to the profibus at the slaves that don't work, and check for reachable partners from the Simatic manager.
Looks like you have master address 1 and first slave address 1?
realy good advice , I will checked
also is neccssary to aranged the nods serialy like 1,3,4,5 etc or I free to arranged it randm like 1,8,6 etc
Many Thanks for Help
You can do whatever you want with those, just keep within the range. Common practice is to use 1 for master.
Dear Bonelss
I have the Master address for Main CPU S7-315 is( 2 )
But this project first project for me with Simens PLC network
Any Help will be highly Appreciate
You can use addresses freely, but as boneless mentioned, I would not use address 1 for a slave (but I don't know if this is a problem).
I always start at address 5 for the DP-slaves. So I can use 1 for my programming device, 3 and 4 reserved for HMI devices.
my bad :).
you might want to post your project, makes it a lot easier to look at.
also, double triple check your termination and end switches.