S7-414H is not showing reading in WinCC

arocon

Member
Join Date
Oct 2006
Location
Dubai
Posts
171
We have used S7-414H PLC with WinCC HMI. one of Pressure transmitter reading is showing zero in WinCC though transmitter is ok.

Could anybody tell me the way of the diagnosis the problem. I am new in S7 & WinCC.

Thanks in advance
 
When you go online with the PLC, do you see an input from the pressure tranducer that isn't 0?

Start at the pressure transducer, make sure it's working correctly.
Examine the signal wire from the pressure transducer for any damage.
Connect to the PLC and see if it's getting the value from the transducer.

We have had some Wonderware HMIs lock up certain numeric displays until we rebooted the PCs. I'm not sure why it happened, but a position field locked onto a number, and even when the value changed in the PLC, the display wouldn't change. Once we reboot the PC, the problem resolved itself.
 

Similar Topics

Dear All We want to communicate S7414-4 H (6ES7 414-4HJ04-0AB0) with yokogawa dcs cs3000 through dp port. would it be possible to communicate...
Replies
6
Views
4,104
We have S7-414H system. We found master CPU all LEDs were flashing. The alarm sequence from diagnostic buffer are as follows: Switchover of...
Replies
1
Views
5,115
hi all ! if any body know how to simulate analog value in S7 414H CPU, please let know the sequence how to do it. thanx.
Replies
1
Views
4,749
I have a customer who asked me to fix a problem in a working site. An S7-414-4H type cpu in redundant rack goes to stop mode once in a week or...
Replies
3
Views
4,324
Good morning, We've had an issue with a couple of servo valves and was wondering if anyone had seen anything similar. After a drop in pressure...
Replies
2
Views
123
Back
Top Bottom