i have 314 siemens cpu
the machine stopped and all plc output modules doesn't give any output .
i checked it and all modules are ok.
when i monitor the online program with simatic manager i noticed
the ob1 doesn't running Monitor signal ( color green which lies below window) still freeze==> can not read data.


so it reads input images but it doesn't make scanning to give the output .


is this a trick from the programmer or what ?
 
If the CPU is still running, RUN lamp is on, SF or BF are both off, but all outputs are off.
Try to force an output.
If it goes on, then you must trace in the program why the outputs do not go on.

If you have a SF or BF, even if RUN is on:
Investigate the diagnostics buffer of the CPU.
If in doubt, export it to a textfile and post it here.
 
What is the part number of the CPU? Does it have a backup battery or a MMC (micro memory card)?

If it has a backup battery, if the red BAF light is on, change the battery. If it has an MMC, make sure it is pushed all the way in. I had a client whose big fingers happened to eject it about 1mm when trying to change the STOP/RUN switch.
 
If the CPU is still running, RUN lamp is on, SF or BF are both off, but all outputs are off.
Try to force an output.
If it goes on, then you must trace in the program why the outputs do not go on.

If you have a SF or BF, even if RUN is on:
Investigate the diagnostics buffer of the CPU.
If in doubt, export it to a textfile and post it here.
thank you for your reply
,the hardware diagonestic of the cpu status is ok no errors .
the error buffer doesn't contain any new errors.
as you say the cpu doesn't make any scan for inputs and doesn't gives new image of output .
i made a simple network with one i/p and one o/p but the cpu reads i/p
but it doesn't process output .
 
Did you try to force outputs?
If RUN led is showing run status, then it is strange if OB1 isn't running if animated.
 
Did you changed hardware config? Or the did the cpu stopped working suddenly?

What colours are the cpus leds? Are all them blink?

Check the IO addresses on hardware module config are the same addresses that you are using in ob1
 
Last edited:

Similar Topics

hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
Replies
2
Views
117
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
168
Hi there, I have an application where I’m required to connect Siemens S7-300 PLC (Profinet) to Allen Bradley Control Logix Remote I/O Rack &...
Replies
11
Views
3,658
Hello guys, Our working machine CPU I am trying to add one logic but when I am click download then warning ⚠️ message coming that Unable to...
Replies
2
Views
1,408
I have ABB ACS 800 Drive being controlled from S7-300 CPU the drive is turning on but the motor is not rotating i have attached the program and...
Replies
0
Views
1,548
Back
Top Bottom