Hello guys,
Our working machine CPU I am trying to add one logic but when I am click download then warning ⚠️ message coming that Unable to copy FB 11.
I write the program in FB 11 and network 39.
Kindly support and help me. Thank you.
Kind regards.
Biti.
Hello guys,
Kind regards.
Biti.
Please post a screenshot of your added network and your error message.
Most of the time in the message box with the error message there is a button for more info about the error, click that and read it.
you are probably trying to use some address outside the supported range of the CPU. like using timer T300 when the highest allowed by hardware is 255
grtz
You may have an address in your FB11 Network 39 that your CPU doesn't support. For example, the CPU 312 CPU only has 256 bytes of M memory (MB0 to MB255 / M0.0 to M255.7), and you put an address of MB256 or higher, or M256.0 or higher, etc. To find out the min/max addressing ranges, open the Module Information on the CPU in STEP 7, or go to Online & Diagnostics in TIA Portal.
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
117
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
168
Hi there, I have an application where I’m required to connect Siemens S7-300 PLC (Profinet) to Allen Bradley Control Logix Remote I/O Rack &...
3,656
i have 314 siemens cpu the machine stopped and all plc output modules doesn't give any output . i checked it and all modules are ok. when i...
3,302
I have ABB ACS 800 Drive being controlled from S7-300 CPU the drive is turning on but the motor is not rotating i have attached the program and...
1,548