How you detect a fault depends on the nature of the fault. A stuck contact on an e/stop is detected by the safety relay seeing one channel open but not the other. A welded-in safety contactor is detected by wiring the NC auxiliary of your safety contactor in series with your reset loop (and of course, making sure you're using the appropriate mechanically-linked contactors so you can't have the NC closed while the main poles are welded shut). A short circuit to 24V on a guard switch is detected by the use of a test pulse. And so on.
I 100% disagree that Cat 4 is "a goal and not a standard". I've put in hundreds of systems that reach Cat 4, many of them externally validated as Cat 4. Many of my clients do risk assessments on their machines and require a Cat 4 safety system implemented. I'll admit to having my tongue firmly in my cheek here, but a decent amount of my company's work at one client involves getting in new machines from the USA and completely re-doing the safety systems :)
On a simple system, you can reach Cat 4 with nothing more than an off-the-shelf safety relay, an e/stop, and some safety contactors. In larger, more complex systems, you might need a full safety PLC to do the job. I've had systems validated with a single guardmaster safety relay, and others with a Guard Logix and multiple remote safety I/O racks. Horses for courses.
Whether or not you can put things in series (and what safety category you end up with) is a very broad question without a simple answer. It depends an enormous amount on the specifics of the system. A general rule of thumb would be that you can put e/stops in series and meet any safety category, but if you put guard switches in series, you can generally only meet Cat 3, and even then it's not a sure bet. Depends on a lot of other factors. Here's another thread that discusses a lot of these sort of issues - in my post #23 there's an explanation of fault masking and how that applies to putting things in series.
Hi all, I'm working on a safety circuit and had some question about fusing. Incoming supply - 120V/15A Power supply - PSL-24-060...
590
Is the mechanism that energize a safety relay, Inductive or Resistive? These are the terminals that are marked as A1 and A2 on AllenBradley, Pilz...
776
Does anyone here have experience with the new GuardLink safety relays? They look like a dream to troubleshoot and work with since its just a trunk...
1,214
Hypothetically we have a machine with safety door switch and a E-Stop. The operator places the work piece into the machine, the door is closed and...
20
7,330
In a new electrical cabinet we have to apply to safety level PLd. We have a circuit for direct online motors. We will be using two power...
2,181