Hello,
If you sign off a safety signature for a machine, can it be used and valid on other processors if the setup is the same?
Thanks
At a purely technical level, that probably depends on what brand you're talking about, and what kind of safety signature you're talking about (software, hardware, etc). In general, in the PLCs I've used, the signature covers the compiled PLC code and the HW part numbers and safety relevant parameters, but not the actual serial numbers of the devices. I've never checked to see if something like IP address plays into this or not. In addition, the safety PLCs usually have multiple signatures available (just SW, just HW, everything, etc)
There's more to safety than just "does this technically work" though, it's far more about the regulations and paperwork, to be super duper sure no one gets hurt, or at least to cover all butts to the extent possible.
In my experience, the safety signature isn't something you sign off on so much as something you note down as part of the sign off process. As you sign off the other machines, you would note theirs as well; might be the same if the machines are identical, but it's hardly any extra work to check compared to the rest of the signoff checklist.
If your question is "do I need to do a safety sign off on these other identical machines as well", then I guess that's up to you (at least in the USA), but my thought is definitely yes. It's possible some parameter isn't set correctly, or something is wired wrong. Regardless, my experience is that it's best practice to verify the function of most safety systems periodically, not just as part of sign off, tho the period varies depending on lots of factors.