saia plc pcd2 m5540 xob 13 error
quaiser
Feb 2018
al kharj
hi,
i have a machine with SAIA model number PCD2.M5540. Recently i am facing issue regarding the run and stop mode. i tried setting the plc to run mode manually... it runs for few minutes and again goes back to the stop mode.. and an error XOB13 is flashed in the display.
i would be very grateful if anybody could help me solve this problem.
http://web.ist.utl.pt/ist11390/AI/PCD1_PCD2_Hardware_Manual_26-737_E.pdf
XOB 13 error seems to be a general one that could be a number of items. Please check the above manual.
https://www.sbc-support.com/en/product-category/archive/programmable-controller/pcd2-cpus-flat-design/mxxx-cpu-units/pcd2m120/
From the IO manual:
An XOB 13 is called in following cases:
■ If module is not present into the PCD slot and Program tries to access it with
‘Direct Access Instructions’
■ During an internal reset of the module
If XOB13 is not programmed then Error Flags is set.
Direct input or output access in IL
The XOB 13 error happens if the PCD wants communicate with the module but it is
not in the slot.
In case of reset of the module (Watchdog UC), XOB13 happens if PCD try access to
the module during restart.
Hope this helps you out.
Regards,
Hi
As mentioned XOB13 can be triggered from several errors .
The history log could indicate at what program step the error appears.
If there is a XOB13 program, it may contain debug information (Diag writes 12 registers containing error info)
Regards
Bardes
Gents, I have a PLC and HMI from SAIA Please, see in the attached pics and tell me how to upload the programs to the PC (PLC and HMI) Tons...
2,272
Questions about an old SAIA PLC type PLC is PCD4 - board RS422 (PCD7.F110) We sold a HMI to replace one but our HMI doesn´t communicate with the...
1,087
hello staff need help again We acquired a machine that has second-hand plc I need to make changes in a skirt plc program PCA1 M54M4 and PCA1...
1,415
Hello everyone Does anyone have any experience with the SAIA PLC type PCD2.M110? where to find (free) software for that Plc? that setting has to...
1,762
Hey all. I don't like to do this, but we've got like a huge thing going on here, and they'd like for me to get it over with as soon as possible...
5,441