SCADA Availability on RF network specs
michaelbsc
Sep 2005
Charleston, SC
Does anyone have standards or industry best practices in a semi-official document for SCADA availability requirements on an RF network? Some of our RTUs miss polls and wireframe (FT VIew 11) several times daily. And operations gets upset if it's not always available. (Understandable) But the power that be don't want to spend the money to get 99.999, they want some supporting documentation that less (say 90%) is tolerated in other places.
Has anyone got some standard? I can't find any good quantitative data through Google. Guess my Google skills are subpar.
It totally depends on your process. Is the com loss an annoyance or does it affect the process? Store and Forward is something you can implement at the RTU. Data logging at the RTU, then do a dump to the MTU every so often.
It is FT View after all, so the could the wire framing be a software issue?
Well, it could be a business risk or safety risk.
Use your company's risk assessment framework to do a risk assessment.
Use the risk assessment to inform business decisions.
I would say if there are no risks, then yes, low availability is accepted.
Alternatively present a business case on how it will save them money.
There's not really a standard, because it's so dependent on what the end user is doing with it. I have sites that need near 100% comms success rates because a flow reading on one site is used to set a pressure setpoint on another. Loss of comms means automatic switching to a less efficient operating mode, which is not ideal.
90% is very low availability. That's over 2 hours a day where you're saying no comms is fine. A properly designed radio network shouldn't have issues like this. Id try to solve these issues by first:
- Setting up a radio pathloss model for all sites on your network. There is free software called RadioMobile for this, which is good enough for this kind of thing. Or engage a specialist consultant to do this with commercial software (expect to pay 3-5k depending on size of your network).
- If the pathloss model shows that comms should work (ideally better than -85dBm but anything up to around -100dBm should work) then investigate why. Hopefully you've got modern radios with built in VSWR and RSSI monitoring. Check there are no issues with antennas, coax, local obstructions. I've seen sites that have been working mostly ok with the antennas pointing 60 degrees off... when aligned properly performance when from OK to perfect. Alignment was hard before the advent of Google Earth. You had to use a compass and paper maps... now, just draw a straight line and find a decent nearby landmark.
If you have sites that have poor or obstructed paths then you may need an additional repeater. Or, with modern IP routable radios, use another site with good coverage to provide a "last mile" point to point link to the troublesome site. A few K for additional radios and installation and problem solved.
Unfortunately all of these require spending some time figuring out the problem, and then possibly spending some time and money fixing the issues. But that in my eyes is much better than simply trying to find a way to say that **** performance is acceptable.
50
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
237
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
64
Has anyone ever seen where you have a tag reading from the plc in scada. In this instance it's just a PEC, I set it up on one scada terminal and...
99
Hi guys, I have experience with PLC to Excel etc...just starting on using intouch scada screens. I have an Excel sheet that uses mainly...
152
