Rockwell converted a running IFIX system to FTView SE for a customer. (By the way, NEVER have them do this. They sell it as a 90% complete conversion, which is now costing big $$ in cleanup).
The old IFIX system used scaling, in the tag database, for the PID SP/CV/P/I/D values. I created a bunch of parameter files for all the PID variables. For the numeric displays, I can just do an expression and divide by 10, but for the SP entry, I see no way to scale the output. The old system used a single tag with integer offsets (F_XX) and since FTView doesn't support that, I see no way except to create tags for every single PID loop and use those in the parameter files.
The old IFIX system used scaling, in the tag database, for the PID SP/CV/P/I/D values. I created a bunch of parameter files for all the PID variables. For the numeric displays, I can just do an expression and divide by 10, but for the SP entry, I see no way to scale the output. The old system used a single tag with integer offsets (F_XX) and since FTView doesn't support that, I see no way except to create tags for every single PID loop and use those in the parameter files.