Scaling Function
Manoj M
Feb 2014
London
59
Hello Experts,
Need your advice on this. I am using Step7 V5.5 SP4 for my programming. I am using FC105 scaling function to scale 4-20 mA signal to 0-375 rpm. Now the customer has changed the specifications and want me to do the scaling in multiples of 5. For example between 4.11 to 4.32mA the speed should be 5 rpm then from 4.32 to 4.53 it should be 10 rpm ad so on and this will follow up to 375 rpm in the multiples of 5. Can somebody suggest me the simplest way of doing this. Please see attached picture for your reference.
Regards
Manoj
Can you say "Change Order"? I would use a PID function. You should be able to accomplish your task by configuring the parameters correctly.
Does the Siemens have a For Next capability? Otherwise you would be using GT & LT statements out the wazoo to watch your input and set the output.
Hello Webhead,
Thanks for your reply. I can use the GT and LT functions but that seems to be the lengthiest solution for getting upto the speed of 375 rpmand if that is the only solution then I have to do it.
Regards
Manoj
Hello Manoj M ,
I do not have development environment right now, but it should work.
Code:
      L     "Analog Input 0 -->27648"  // 4-20 mA
      ITD
      DTR
      L     1.843200e+002    // Half step length  ((27648 / 75 ) / 2))
      +R
      L     7.500000e+001    // total step's
      *R
      RND
      L     L#27648
      /D
      L     5
      *I
      T     #RPM
Regards.
Hello SHKODRAN,
Thanks for your help. I will give a try to this logic and will let you know the outcome.
Regards
Manoj
Hello SHKODRAN,
Thanks for your help. I have tried the logic you said and it is working like a charm.
I cannot thank you enough for this. Really appreciate this.....
Hi all, i am trying to scale a 0 - 1000 analogue input to a -10000 to 10000 output with 0-500 been -10000 to 0 and 501-1000 to 0-1000 is there...
2,898
Hi All Omron Experts I need help to create a FB for Omron PLC CP1L-E Task: Detect and Monitor Oil Level in a Hyd. Tank Using Incorporated...
1,745
Hi Friends, Please, who can tell me the Function Block used for scaling 4-20mA to say 0-200PSI in Mitsubishi GX Works3?
7,319
Hello Experts, I am using Step 7 V5.5 Sp4 for my project. In my project, I was scaling 4-20mA signal to -180 to 180. As of now it sounds like a...
1,715
I have written a scling block to scale real values in the PLC code to integers for use on analogue output blocks, I want the scaling block to...
2,334