scaling in ab 1734 4-20ma analog input card
jcperdue
Feb 2013
Indianapolis, IN
In the literature for the card. It says scaling for the enginieering parameters can be done in the card. It shows what the raw data for 4 and 20ma will appear as. I'm going to us 0-100 lpm flow meters on those inputs. Can I really go into the configuration for the card and put 0 for the 4ma and 100 for the 20ma and do my scaling that simply. This is kind of what the literature implies, nowhere does it just come out and say it.
Yep, it is that simple.
There is a caveat though: scaling directly within the module and setting the Low Engineering to 0 LPM for a "transmitted" current value of 4mA will not accomodate provisions for "electrically open circuit" conditions sensing (the sensor "outputs" 0 mA); the CPU will not be able to "detect" the "zero current" value since the proposed calibration "ignores" anything less than 4mA and accordingly placing "0" within the hardware defined tag.
Thanks for your help. I'm glad it is that easy. I'm adding these flowmeters, but I'm not an indepth programmer. This will really make my task easier. I understand what you are saying about open circuit detection. I'll have to keep that in mind
I have everything set up for vibration monitoring with the code in Controllogix 5000. The thing is that I am not able to read values SCADA in mm/s...
28
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
195
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
664
402
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
229