Scaling
al_d
Nov 2004
36
Im using an OMRON CQM1 PLC. Im using an analog probe to measure products and if they are to small or to large they must be rejected. For this a scaling (fun(66)) function is needed but how does scaling work?? What does it do??
You do not have to use the scaling function if you wish. Scaling is normally used so that SCADA systems and screens can read straight BCD numbers out of the PLC or you can scale amps for example and do not have to work out what the value is from the hex value.
If your analogue card uses 0-4000 for full range, you can compare at 1000 for example and then use a less than flag to indicate below 25% input. This can be your alarm without scaling.
Chaeck the manual for the numerical range of the input card and go from there.
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
186
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
639
372
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
221
Hi all. I'm working on a rehab and I'm trying to figure stuff out. See screenshot at the bottom. Local:5:I.Data[6] in BTD instruction is a...
715
