Hi friends;
I purchased a new analog module ALG 223. I connect the transmitter 0 to 87 PSIG. Set the configration as follows
low=0000
high=32000
at 4 mA the counts are +0000 and at 6.08 mA counts are 4136 (unable to apply 20 mA right now)
Now i attached a image which i apply for scalling according to following formula
EU = ((EUSpan x (DATA - DataOffset))/DataSpan) + EUOffset
ProcessValue = EU / FACTOR
Scalling applied 0 image starts for done scalling Variable RAW have counts from %AI.
at 6.08 mA the reading should be 11. somthing but it shows 14.0 a three psi error.
I am confuse to done it please guide me how i get and which block step by step i apply to get the right value.
I use the mathmetical equation as
FACTOR = 10
Data @ 4 mA = 0000
Data @ 20 mA = 32000
DataOffset = 32000
DataSpan = 32000
EUOffset = 0 x 10 = 0
EUSpan = (87 - 0) x 10 = 870
DATA = 4136 counts from %AI
EU = ((870 x (counts - 000)) / 32000) + 0
But a guy use the following method and i am confuse how he calculate
FACTOR = 10
Data @ 4 mA = 6240 // this one ???????
Data @ 20 mA = 31208 // this one???????
DataOffset = 6240
DataSpan = 31208 - 6240 = 24968
EUSpan = (60 - 0) x 10 = 600
DATA = 18975
EU = ((600 x (18975 - 6240)) / 24968) + 0 = 306
Process Value = 306 / 10 = 30.6 psig
Secondly for every transmitter the scalling is diffrent?
please i need a explanation for understanding
Hope you guys help me to considered my example
Regards
Sir;
Oh sorry i do it now it value is 11.2 PSi.
Sir i want to ask where this type of following calculation is used?
DataOffset = 6240
Secondly if i use in enhansed mode and set -2000 to 32000 then the logic which i applied working?
Sir u see images i want to ask that i do correct work or it replace by a short logic? Please guide me
Regards
Hi Guys I'm using Vijeo Designer as HMI, and we're monitoring the water levels in a water well of 6 meters deep. I created the water well in...
1,322
Hello friends; I am new with Mitsubishi system. I need some example to handle the 4-20mA by using FX-2n-4AD which is attached with FX-1N-14M...
3,560
Dear All; Good day. I have a flow meter range 5-70 Cm/hr and out is 4 to 20 mA. first i want to ask how i calculate that at 13 mA what is flow...
1,700
Hi All I am doing a Tank Gauging project. In there all the tank parameter like level , temperature , pressure are coming into a master...
3,880
i'm a newer in PLC programming... anyone please help me about how to do analog scalling in PLC, please sent me an example the ladder for this...
3,288