Scalling for analog input module - SLC 5/04
ckchew666
Aug 2003
Malaysia
591
Guys,
I'm checking on some of the analog input at the SLC 5/04, I couldn't understand some input (min & max) & scaled input (min & max) settings.
1) For example, I tried to inject 4-20 mA into one of the analog channels (completely remove all the 2 cables at the channel), I managed to get the below reading at RSLogix 500:
Inject (mA) Value
4 3271
8 6545
12 9818
16 13094
20 16368
But at the SCP instruction
Input = I:6.3 (3150)
Input Min. = N7:56 (3175)
Input Max. = N7:57 (9007)
Scaled Min. = N7:66 (0)
Scaled Max = N7:67 (5000)
Output = N7:174 (-21)
a) I taught the Input Min shall follow the inject value of 4 mA, which is 3271?
b) The Input Max. value shall follow the inject value of 20 mA, which is 16368?
The field device is a 4 - 20 mA pressure transducer.
2) while for another analog input module;
Inject (mA) Value
4 3274
8 6551
12 9827
16 13106
20 16383
Input = I:7.1 (0)
Input Min. = N7:58 (1507)
Input Max. = N7:59 (0)
Scaled Min. = N7:68 (0)
Scaled Max = N7:69 (5500)
Output = N7:160 (5500)
c) The Input Min. is larger than Input Max.?
The field device is a pressure transducer using 4 - 20 mA.
Both analog input module is 1746-NI4.
Your assumptions are essentially correct. The previous programmer may have been getting creative:
1) He may have found the pressure transmitter in the field had some error or drift, and put in actual data and transmitter display readings to "calibrate" the signal.
2) The second transmiter may have been a suction side transmitter and he wanted to have the engineering units display negative.
There is, of course, also the possibility that he didn't know what he was doing.
I don't a lot of experience analog cards. This IFE analog input card has a spare channel I'd like to use. Today I used a 4-20mA signal from a...
4,903
Hello friends; I am new with Mitsubishi system. I need some example to handle the 4-20mA by using FX-2n-4AD which is attached with FX-1N-14M...
3,557
i'm a newer in PLC programming... anyone please help me about how to do analog scalling in PLC, please sent me an example the ladder for this...
3,287
Hi friends; I purchased a new analog module ALG 223. I connect the transmitter 0 to 87 PSIG. Set the configration as follows low=0000 high=32000...
1,551
Hi Guys I'm using Vijeo Designer as HMI, and we're monitoring the water levels in a water well of 6 meters deep. I created the water well in...
1,321