Sculy relay logic for sticky bits

jandrul

Member
Join Date
Jan 2013
Location
NY
Posts
6
I have found some logic in a PLC (90's vintage) controlling our hot oil furnace which attempts detect a stuck bit ! I think the theory was that bits could get stuck much like a relay. Anybody out there seen this before ? Anybody have issues with stuck bits ? This logic is currently bypassed as it uses an external relay for the test which ironically fails too often.
 
stuck bit usually means burnt input/output or memory error, if there's no forcing or logic error. that would cause plc to raise fault, so i don't really see the point in detecting stuck bit...
 
I have found some logic in a PLC (90's vintage) controlling our hot oil furnace which attempts detect a stuck bit ! I think the theory was that bits could get stuck much like a relay. Anybody out there seen this before ? Anybody have issues with stuck bits ? This logic is currently bypassed as it uses an external relay for the test which ironically fails too often.

Yes, but only bits that are accessed from a remote device. I commonly write code to avoid "stuck button syndrome", so that if comms are lost or if only one packet gets lost (the one to turn of an HMI button bit for example), then the program ensures that no unexpected or neverending action takes place.

If the "stuck bit" isn't written by an external device then all of this is unnecessary, since bits in a PLC can't get "stuck" on or off all by themselves.
 
you know what, I have seen this problem in an old S5-95u. The 24v power supply started to fail - The way it failed caused a floating voltage on the negative 24v which was grounded, consequently causing the logic to fail sporadically. I was called to site to investigate some strange goings on with a palletiser and monitoring online found inputs remaining at logic 1 with no 24v on the input; and vice versa...I found the problem because the HMI went up in smoke about 1 hour after getting to site......:)
 
I have found some logic in a PLC (90's vintage) controlling our hot oil furnace which attempts detect a stuck bit ! I think the theory was that bits could get stuck much like a relay. Anybody out there seen this before ? Anybody have issues with stuck bits ? This logic is currently bypassed as it uses an external relay for the test which ironically fails too often.

Yes, this is common (probably required based on your reading of NFPA) in Burner Management Systems and other Safety Systems.

Use a Solid State Relay in place of the mechanical relay and you won't have to bypass the logic, BTW.
 
Last edited:

Similar Topics

Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
114
Hello, I need assistance in making a Relay operation that follows the given parameters: -if S1 is switched and S2 is at off, the Lamp 1 will be...
Replies
3
Views
114
Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
Replies
14
Views
442
I have an application where I want to use a safety relay in combination with a flame detector as the sensing element. The flame detector has relay...
Replies
23
Views
1,094
Back
Top Bottom