Serial String Checksum?
ViperDaSnake
Mar 2010
Texas
45
I am reading a serial string into a Red Lion DSP.
The string has a 2 character check sum at the end of the string to confirm that the string is not corrupt.
I need to understand how they go about getting the value so I can error check the string.
I also want send commands to the device but I need to send the proper check sum based on the command I send.
I contacted the manufacturer of the device (Sullair Compressors) and they do not remember how they calculated the check sum?
I've googled quite a few possible solutions but I am just as confused now as when I started. I know this will not be easy but I am willing to learn...
Below are real world captures from the device. (Sullair Compressor)
According to the manual, the last two numbers are the checksum based on all the previous numbers listed here. So in the first string, 50 is the check sum.
Does anyone know how to calculate this?
Let me know what else I could provide to help you help me.
03M50
01N0,110,3781,B,A89
03N461,111,3775,t,AE6
03M50
01N0,110,3781,B,A89
03N456,111,3775,t,AE2
Curtis
"They don't remember" ? :)
My first guess is that the numerals are treated as values, while the letters are treated as the ASCII equivalent. The checksum is then expressed as a hexadecimal value in ASCII.
Uppercase "M" in ASCII is a value of 77 (decimal), for example. So
"03M" is 0 + 3 + 77 = 80 (decimal) = 50 (hex)
But that only works for the first example.
Are these from a User Manual you could share, or do they come from a protocol analyzer ?
Another online tool I use for cyclic redundancy check calculations:
http://www.lammertbies.nl/comm/info/crc-calculation.html
The examples given are from a protocol analyzer(red lion data station plus.) These are real world captures.
I have a manual that I would rather not post for copyright reasons, but it basically says that the last two in the string is:
xx - two character checksum, based on all characters after STX
With no further information given about the checksum.
STX is the "Start of Transmission" or "Start of Text" character, which is always 02 (hex). It's not printable as ASCII.
I don't see any spaces or squares where the STX character might be, nor any ASCII "02". Does the Data Station Plus have a driver for Sullair, or is there some kind of "serial monitor" feature it has ?
Examine two similar command lines:
The difference between the values in the first segment is 5, and the difference between E6 and E2 is only 4. This suggests that the Checksum is not strictly additive.
I omitted the STX for clairity:
HyperTerminal
:)03M50
:)01N413,111,4193,t,AF0
:)03N211,111,4196,t,AEF
Looking for trends?
01N298,112,4193,t,AE4
01N288,112,4193,t,AE5
03N221,111,4196,t,AEE
03N206,112,4196,t,AEA
01N312,110,4193,t,AF3
I think I figured it out. It's a type of Longitudinal Redundancy Check, also called a Block Character Check.
As described in the Wikipedia article (hangs head in shame for resorting to it)
1. Convert each character from ASCII to decimal.
2. Sum all the byte values.
3. XOR the result with 0xFF (hex) to cut off any bits over 8.
4. Add 1.
5. AND the result with 0xFF (hex) in case the result was over 8 bits,
6. Convert the result to ASCII.
The first string in the most recent example sums up to 1052 (decimal) = 0x041C (hex) = 10000011100 (binary).
10000011100
00011111111 XOR
11100011
1 ADD
11100100
11111111 AND
11100100 (binary)
That's 0xE4 (hex), so that's the checksum.
I ran a couple of these in a spreadsheet and they all work out correctly.
Ken would you be interested in sharing those spreadsheets?
Bernie Sullair doesn't even tell their field support guys this info. I did a job for them about 5 years ago and after working with their communication engineer I gave up on any further jobs with them.
All I did was use the spreadsheet to convert ASCII to decimal using the CODE(cell) function, then SUM the column. I couldn't figure out how to do bitwise XOR or AND so I did those by hand.
Every compressor maker seems compelled to build a custom serial protocol, it seems !
Step 3 above should be "because XOR 0xFF is how LRC calculations do their thing".
Those damn Xor and And are what I was having trouble with. I hate having to hand calculate anything When we have PC infront of us.
Interesting. I was thinking at first glance the end calculation after the addition was
(100h - (added result && FFh)) && FFh
The boundary instances (0, 1, FFh) work fine with this also.
Hello, I have a scanner connected to my Allen Bradley PLC and i can receive the scanned barcode in my plc as a String. Now i need to transfer...
1,959
Found an awesome point of sale for $500. It sends an ascii string when a product is sold. Need to convert this into a number between 0 and 255 or...
2,278
I have a device that reports back multiple data points in a string seperated by commas. Is there an easy way to extract each data point to a tag...
2,335
Good Morning all, I am reading a serial string in Beckhoff twincat from an RS232 motion sensor. My problem is that the motion sensors...
3,074
Dear all, Could anyone advise me on what messaging method under MSG function of RSLogix5000 should be used to send out a data string (ASCII/HEX)...
5,474