Setting IP in PowerFlex 755 without HIM

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,045
I set the rotary switches to .123 so I could connect with DriveExec or CCW, and then I changed the IP to what I really wanted (10.1.32.32), disabled BOOTP, turned the rotary switches back to 777, and cycled power on the drive. This worked for the first drive, but it is not working with the other two. When I cycle power, it goes back into BOOTP. I have to set the IP with rotary switches to connect again. Am I missing something?

Oh, and BOOTP doesn't work. It fails to set it, which is why I am trying to do it through software.
 
Last edited:
I've have a string of issues after converting to Windows 10 where the software won't turn Boot-P off properly. The work around I've been using has been to use Boot-P to initially set the IP address, but then navigate to the device with CCW or DriveExplorer (or whatever software I can navigate to the drive with to set parameters) and change the parameter from there. It's slightly annoying, but it also allows me to go ahead and check the other parameters and make a backup while I'm there, so not a complete waste.
 

Similar Topics

We have a PowerFlex 755 application using an incremental encoder for feedback. Is it possible to reset the Feedback Position to zero or a set...
Replies
1
Views
2,299
Good Morning , I am trying to setup a PowerFlex 755 and I can't get my head wrapped around the digital I/O setup concept. It doesn't look...
Replies
3
Views
3,901
Hello, I am playing around with a Powerflex 525, I am able to run the drive via RSlogix 5000 over ethernet. I am curious on how to set drive...
Replies
3
Views
672
I have a PowerFlex 753 V14.002 connected to an L8X processor for control of it. I am trying to add a data link but I have not done so before with...
Replies
3
Views
2,135
Hello, So I am trying to set the parameters of a pf523 with a Micro850 PLC all done over CCW. I've set it up before with RSLogix5000 where when...
Replies
1
Views
2,453
Back
Top Bottom