setting servo motor torque fault level
unsaint32
Oct 2012
minneapolis
365
We have a servo motor that moves a traverse arm. At one point the arm got jammed and the motor kept turning and it actually bent the steel plate arm before the axis faulted out.
In Rslogix5000, in axis properties, under Fault actions, I am trying to change the custom stop action attributes to make the fault happen sooner or at a lesser torque applied.
My question is (referring to the picture attached), should I raise or lower the stopping torque value & should I raise or lower the stopping time limit?
thanks.
neither
go to the limits tab
look at "manual adjust"
you are looking for Peak Torque and Continuous Torque
or in the Custom Limits
Torque Limit Positive
Torque limit Negative
WARNING
Read up on the effects of changes to these parameters in the manual
an incorrect change will cause the axis motion to become slower and possibly overshoot - especially when under load
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/motion-um001_-en-p.pdf
Note: these parameters can also be changed by using a SSV instruction
Are you monitoring the axis Torque and position error?
if not then set it up so they are monitored
- DriveMotor Tab
real time information​
you can then trend the torque and position error and write your own code to react if the torque is too high for too long
Hi All. I am setting up an Omron 1S Servo Motor to drive a conveyor. It goes forward 200mm, pauses and repeats until it is stopped. However...
762
Hi, I programmed and installed a new ultra3000 servo drive for a press feeder. I have the operation mode set as "Follower" and it operates fine...
3,080
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
876
SELECTED NEW FILE SELECTED PROCESSOR TYPE SELECTED I/O CONFIGURATIONS IM UNABLE TO CONFIGURE MY I/O’S. I HAVE A PAPER COPY OF A PROGRAM AND I...
88
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
243