Setting up Generic Ethernet Module

lncabin

Member
Join Date
Nov 2014
Location
LA
Posts
8
I've got a device sending me a <STX>data1;data2;...;datai<ETX> message through ethernet. Is it possible to determine the assembly instance information from this message?
 
I assume you're using ControlLogix.

In this case "generic Ethernet module" is a misnomer. It should say "Generic EtherNet/IP Adapter Device".

Such an entry in the I/O tree of the ControlLogix/CompactLogix project has to be an EtherNet/IP Class 1 Adapter. It's not literally "some generic device on Ethernet".

You probably need some kind of ASCII-to-EtherNet/IP gateway, or you need to write an application for the generic sockets feature.

What exact device is it ?
 