Sharing power for outputs
>:D
Aug 2022
ohio
I recently acquired a micro830 48qwb, and it has relay outputs bult in. For outputs 0-6, they all use 24vdc. To save on space and terminal blocks, could I just jumper the 24vdc between each output relay? I'm putting the loads on the "com" side of the relay output, before going to neutral, if that makes sense.
Also, I want to jumper my input commons together, as they're also all 24vdc. I assume there's no problems with that?
Thanks.
Thanks.
The 24VDC outputs are transistor outputs, the rest of the outputs are relay.
The transistor outputs will not work in negative polarity wiring - putting the power on the output terminal and trying to get the signal on the COM terminal. Also, there will be a little leakage current and wiring 6 together might be enough to trigger the output device, even if pulsing repeatedly.
I would wire the 6 outputs to interposing relays and do what you want to do with those relays.