Sharing Tags Between AB Contrologix and Compactlogix
Coachman
Sep 2006
Maryland
97
I have a Plant that producing a material that another plant about
300 yards away uses .I would like to keep track of the material
that is produced and also the amount that is used. Is there a way
that I can share tags between a Contrologix and a Compactlogix.
I would like to display this usage on HMI's, but I have to
do a little bit of math,that would be easier in the PLC.
Any Ideas?
Thanks in advance,
What version of RS5000 do you have?
If you have 15 or 16, I can post an example.
If not, I'll walk you through sharing the tags.
Thanks CroCop,
I have Version 15. You can go ahead and post an example, and
give a small explanation. I really appreciate it.
The producer plc is easy. Just create a new tag that's an alias for the data, then click on tag properties and make it a produced tag.
All the work is in the consumer plc, you need to go to your ethernet module, right click and add module, add the module of the producer plc, then right click on the producer ethernet module and add the producer processor, then go to the tag editor of the consumer plc and add a tag, the tag type must be the same as the producer tag. Right click on the tag, go to properties, and make it a consumed tag, you will have to know the produced tag name, spelling and case must match.
I want to make an application in C# .Net to read Tags from CitectScada (Local variables, Variables tags, Digital Alarms ...) so that I can process...
1,601
Usually my projects with multiple HMI's have the HMI's displaying different controls for the section of the machine it's mounted to. I have to...
3,643
Hi everyone, I am working on a project that needs to expose the SV (Set Value) of a temperature controller to a SCADA system. SCADA <-...
165
Hi, We don't do many Rockwell projects but recently did onw with a Control Logix and Panelview. What files do customers expect when you send...
264
Hi, I recently acquired a micro830 48qwb, and it has relay outputs bult in. For outputs 0-6, they all use 24vdc. To save on space and terminal...
1,517