short circuit monitoring on 24 dc DI modules
mvlrao
Aug 2003
DUBAI
Has anybody used to for short circuit monitoring with 1756-IB16D,24vDC DIGITAL INPUTS(Diagnostic modules).Manufacacture talks about open circuit only.
You can do it with an analog card and a couple of resistors at the
feild device. You can detect on, off, open, or short.
What is the difference between a "short circuit" and an ordinary True condition on an Input module ?
As far as I know, there is no 'Short Circuit Detection' (SCD) on the diagnostic input modules. There is however, 'Open Circuit Detection' (OCD).
Ken succinctly stated it above, that you really cannot determine a field-wiring short on an input module, but didn't get into the 'Open Circuit Detection'.
Basically, for the diagnostic input modules, OCD must be first enabled in the module, for a specific channel, and then, you put a loading resistor across the field device. Note, that the loading resistor may not be required if the field device is a solid state switch that has some leakage. The module will then be looking at all times for current flow... tiny current = device is open, large current = device is closed, no current = there is an open in the field wiring (or the leakage/loading current is insufficient).
Decent 'burglar alarm' type systems do indeed employ both OCD and SCD, but as stated above, it's a bit more complicated, and requires an input that can resolve 4 states.
Hi group! Repeatedly found answers to some questions in the PLC's programming world, now I decided to ask the question directly) Now I am...
22
4,276
Hi, I use Allen Bradleys 194e serie as load switch for my cabinets. The technical data confuses me, it says: On the general data it says...
2,017
Hi, I'm a little bit confused on how understand the short-circuit ratings on some components in my cabinet and hoping for some advise. I have...
1,933
Hello, I have a customer with a ABB ACS601-0025-2-000B1500001. I cannot seem to find a good troubleshooting manual online. This is one vfd...
1,412
I'm looking at Profibus DP repeaters, and have been reading datasheets and user manuals. The website for the Procentec model B1 repeater refers...
1,481