Siemens 8 Channel Analog Input Card - SM331-7KF2-0AB0 - SF Fault

DenZ_P

Member
Join Date
Jun 2016
Location
SomeWhere
Posts
64
Hello Experts,

I need your help about this issue of mine about my Siemens Analog Input Card SM331 having SF LED lit. I know this is system fault.

Troubleshooting done:
- Checked Power Supply - OK
- Replaced with known good spare of AI Card - Still have SF LED lit
- Removed cards in the Rack One by One and put it back one by one also. There is no SF LED lit until i put back the last card which is the AO Card.


What's also weird about this is that it is always that 2nd rack channel next to the IM153 that is having this System Fault even though i have replaced with other SM331 card.

Also i cannot received any signal coming from my 7th and 8th Channel with this AI Card which is 3-wire Level transmitter.

I hope you can help me! thanks!

AI Card with System Fault.jpg Communication Ok.jpg
 
Hi,

Did it work OK before the fault went up.

Did you check the range blocks on the side of the module match the configuration made in your software.

gr. John.
 

Similar Topics

My company is commissioning a new machine and we're having a few issues with I/O Channel errors. My Italian colleague took a screen shot for me to...
Replies
6
Views
2,365
hell-o its me again!!!! i was wondering if some one can disipate some doubts i have. made some tests with the sfc13 and can read the: Station...
Replies
3
Views
3,609
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
182
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
145
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
304
Back
Top Bottom