Siemens AO strange or stupid problem
spaderkung
Aug 2007
South Sweden
389
Hi all!
On my system with a S7-319 and a couple of IM151 nodes I do not get the AO cards to work.
The fault appears on all nodes... DI, DO, and even AI after the same PM as the AO is on are working fine. Tried "forcing" QW to rule out program error.
AO configured 4-20 mA. Also tried 0- 20. Always 0 mA measured between 1 and 3 (5 and 7). (And the actuator does not move either). No other connections to card. Tried other AO cards of same type.
No profibus errors.
AO card: 6ES7 135-4GB01-0AB0.
Grateful for any comments.
Try to use the ET200S configurator and put in your terminal modules and cards. There is a button for a potential overview there somewhere. Could be an evil terminal block that breaks the 24V supply.
Kalle
Thanks.
Found some diagnostic setting and found that there was an "wire break". After reviewing the electrical drawing the error was corrected - a combination of broken fuse in the ampere meter and switched actuator connections...
That was my first thought.
Somehow the mA fuse is always blown when I get my meter back after having loaned it to someone.
A tip: Always have a 250-ohm resistor at the ready in the toolbox. You can quickly hook the resistor up over the output terminals, and then see if you can measure 1-5 volts over the resistor.
Hi all, We have a system that comprises of a Siemens HMI talking to 5 Siemens 300 series PLCs via MPI. The PLCs and the HMI are about 50m away...
2,971
Today I connected a new KT600 to a Siemens 317F safety PLC to display some basic information. This all worked fine and was connected via...
3,129
Recently i encountered a very strange problem with a 314C-2DP cpu, the problem i have is with the internal inputs. Right now i have this cpu on my...
4,675
Hello, I am using 331-7KB02-0AB0 AI 2X12 bit module. Input address are PEW 200 and PEW 202...Both are configured as 4-20mA. Now when going...
18
15,807
Hi everyone, I had a strange problem with TP 070 panel display yesterday. After I downloaded my project ( which has 4 screens) I noticed that in...
7,208