Siemens CPU 315-2DP Troubleshooting

You can try for test. Take IM151-3 module from other non working cabinet to first cabinet Connect profibus cable and power to this other IM151-3 module (don't forget end resistor of IM151-3) Dont't change any slave dips and don't connect any IO-cards to IM-module.
If CPU detects this other IM151 module, but says faulty (as there is no configured IO cards connected) then problem is on cabling (or in first cabinets profibus connector outlet) after first working cabinet.
If it still says that for IM151-3 no available then there is other error.

Just wanted to respond back to this. We did this and it helped us narrow the problem down and eventually fix it. Thank you very much!

It's funny because I do things like this to troubleshoot all the time, but I think getting used to new software and protocols and processes threw me off my usual track.

So the electrician had replaced the Profibus cable between 1 and 2 and had replaced the connector at 2. What we found was yes, the IN side of 1 worked, but the OUT side did not. They didn't have any more connectors on-site so what we ended up doing was swapping connectors with 1 and 6, since 6 was the end of the line and didn't need an out.

We got everything coming in and talking!

Thanks a ton for everybody's advice on this! I really appreciate it.
 
Almost every Profibus problem I have ever encountered, was the cabling and terminations. 1.5 megabaud is kind of the default for most industrial sites. I have been to some where they slowed everything down to 9600, just to get things working. Siemens used to sell a handheld tester, was expensive as most Siemens stuff is, but now they have been discontinued, and are several thousand dollars. 1708614605551.png
 
You can buy Profbus connectors in eBay at a very low cost. It is a good idea to keep some spares in the warehouse.
Great you were able to fix your problem.
 
You can buy Profbus connectors in eBay at a very low cost. It is a good idea to keep some spares in the warehouse.
Great you were able to fix your problem.

Yeah we saw that. We got some ordered in case it comes up again.

Almost every Profibus problem I have ever encountered, was the cabling and terminations. 1.5 megabaud is kind of the default for most industrial sites. I have been to some where they slowed everything down to 9600, just to get things working. Siemens used to sell a handheld tester, was expensive as most Siemens stuff is, but now they have been discontinued, and are several thousand dollars.

Yikes. Yeah according to the guys at the plant the system has worked with minimal issues for 15 years or so. Seems fairly solid. Sounds like a power module went bad which fried some stuff and caused all this.

I didn't realize you need a special USB connector to get into the PLC directly. Luckily they had some kind of modem module next to it that I was able to get into with a USB printer cable. Siemens quoted us on their special USB cable and it's $740. :ROFLMAO: No thanks.

Also their software licensing costs seem to be pretty ridiculous. I thought Rockwell was the worst but looks like Siemens isn't too far behind.
 
Thanks of informing that troubleshoot worked.
Was profibus connectors older screw terminal type or newer knife type?

Sound like that you mean MPI/Profibus RS485 programming adapter with USB connector.
 
Thanks of informing that troubleshoot worked.
Was profibus connectors older screw terminal type or newer knife type?

Sound like that you mean MPI/Profibus RS485 programming adapter with USB connector.

They were the knife type.

Yeah that's correct, their RS485-USB programming adapter.
 
I never noticed that caviat. Never tried it.

I carry a Siemens A2 anyway, but for the OPs need it would work fine.
 
I never noticed that caviat. Never tried it.

I carry a Siemens A2 anyway, but for the OPs need it would work fine.

That's great actually. We'll probably try to pick one of those up in case we have to go back there. Definitely beats paying the $740 :ROFLMAO:
 
I didn't realize you need a special USB connector to get into the PLC directly. Luckily they had some kind of modem module next to it that I was able to get into with a USB printer cable. Siemens quoted us on their special USB cable and it's $740. :ROFLMAO: No thanks.

Also their software licensing costs seem to be pretty ridiculous. I thought Rockwell was the worst but looks like Siemens isn't too far behind.
I think for the old Simatic Step 7 (as well as the new TIA Portal) Siemens allows the download of an installation that works for 20 or 21 days.
Also, there are alternatives (non-Siemens) third-party USB to MPI adapters. One of this forum's members has an online store which offers this hardware for a more reasonable pricing.

Edit: Form this member...

geniusintraining

www.PLCCable.com
 

Similar Topics

Hi We were having a few power cuts and the CPU would not work. I had to reset the memory and he CPU would read from the memory card and start...
Replies
13
Views
3,163
Hi, Can anyone explain the difference between rebooting a Siemens CPU 315-2 PN/DP, either by setting the switch into stop and back into run...
Replies
5
Views
2,684
I have a Siemens S7 300 CPU 315-2 PN/DP PLC and CP 342-5. IM Module is configured via ethernet port. I have two profibus network. One on CPU and...
Replies
3
Views
4,138
Hi All. I'm creating several diagnostic screens for the maintenance personnel, displaying the I/O status. Do you know if it's possible to get...
Replies
4
Views
3,707
Hi i Have an OP7 [6AV36071JC200AX1] and a CPU s7-315 DP [6ES73152AF020AB0] I'm communicating between the two via DP, i need to set up the CPU so...
Replies
3
Views
1,403
Back
Top Bottom