Siemens CPU S7-315 DP to OP7
FoolishMantle
Jan 2015
Stoke-on-Trent
Hi
i Have an OP7 [6AV36071JC200AX1] and a CPU s7-315 DP [6ES73152AF020AB0]
I'm communicating between the two via DP, i need to set up the CPU so that if communications is lost between that and the OP the CPU will go into STOP mode
Theres the PG on the network PC with which im programming the CPU [using Step7 and DP communication cable], other than that its just the CPU and OP7 connected with a DP cable.
I've opened up Block OB87 but i dont know how to wirite the program etc
So,is there anyone who can shed any light on how to get the CPU to go into STOP, if the communication to the OP is lost?
Mant Thanks
First of all, why do you want your PLC to stop? IMHO it is always best to keep the PLC running and set all outputs to what you consider safe.
If you remove OB86 from your program, the PLC should stop. But again, I don't think this is something you want.
I've been told the OP has an intermittent comms fault
[it'll drop comms then back again]
I've had some experience with siemens programming but not alot, i figured i could either make a log of comms error or make it stop the CPU [is a spare CPU so it wont affect anything if it stops]
Easier to make it stop the CPU if theres a comms failure, then i can confirm if its the OP or something else
I would rather use SFC51. It allows you to check the status for each DP slave.
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
749
Hi We were having a few power cuts and the CPU would not work. I had to reset the memory and he CPU would read from the memory card and start...
3,163
Hi, Can anyone explain the difference between rebooting a Siemens CPU 315-2 PN/DP, either by setting the switch into stop and back into run...
2,685
I have a Siemens S7 300 CPU 315-2 PN/DP PLC and CP 342-5. IM Module is configured via ethernet port. I have two profibus network. One on CPU and...
4,142
Hi All. I'm creating several diagnostic screens for the maintenance personnel, displaying the I/O status. Do you know if it's possible to get...
3,708