siemens FM350-2 question
panthripu
Mar 2004
228
Hi
Once again need your help.Looking for information about module FM350. We observed sometimes the module is counting negative value starting from zero, which is creating problem. After going through the DB assosiated to it , it has been seen that bit 40.5 is true (direction counter down) , But unable to find out what make it true. How can I reach to its origin?
use the cross reference reference data.
You should also check for byte/word/sword references that overlap the bit.
One more question regarding FM350-1. I got used siemens PLC configuration S300 + FM350-1. PLC is working well, but I have problems with FM350. I need to test it if it is ok.
So, when PLC starts it's (FM350) SF led is ON and then it is OFF. So everything is ok with module configuration and in general it's burned. I changed module control to Hardware Gate to be able start and stop counting using I0 and I1. So as for me it should LED when I put signal on I0 and I1, but it doesn't. All LEDs are off. So how can I test the module? Tried load simple example of using FM350, but I didn't get any data from encoder.
Also tried to load wrong configuration to module and it's SF was ON. So module sees configuration and react.
MY configuration is:
Gate signals: Level-Controlled
Signal type: 24V initiator
Operating mode: Continuous
Gate control: HW Gate
P.S. ask details if my english is not clear enough.
For a revamp we will have a configuration with S7 1500 and FM350 in ET200M on profinet. Will the FM350 work? Because I see in Siemens Tia...
2,748
We are currently encountering configuration problem with FM350-2 used for counting and totalizing functions. When we configure the FM350-2 and...
3,183
Hi All, First time I have ever worked with encoders and I am having a slight issue. The encoder is set up counts up and down and works well for...
2,035
Hi guys, I'm quite new to the world of encoders and as such, I'm not sure what the difference is between the Siemens FM350 & the SM 338. Can...
2,387
Does anyone know where I can get the installation cd or where I can download the software for siemens module 6ES7-350-1AH01-0AE0? I have the...
2,925