Vivi,
Now that you have an external power supply, you DO NOT use the Siemens PLC internal power supply. Instead, connect your new power supply where the "battery" symbols are on your Siemens wiring diagram.
For example, connect your new 24 VDC power supply "-" (minus) terminal to the Siemens S7 PLC terminals 1M and 2M. Then connect your 24 VDC power supply "+" terminal to ALL of your sensors and input switches. You will need to run many "+"wires, or run one "+"wire that jumps from sensor to sensor or switch-to-switch.
Also connect your new power supply "+" to the Siemens S7 PLC terminal L+, and connect power supply "-" to Siemens S7 PLC terminal M.
Because you will have two or more wires connecting to your power supply terminals, you will need a way to split 1 wire into many wires. You can use some "wire nuts" (wiring terminal connector devices) for that purpose.
Now that you have an external power supply, you DO NOT use the Siemens PLC internal power supply. Instead, connect your new power supply where the "battery" symbols are on your Siemens wiring diagram.
For example, connect your new 24 VDC power supply "-" (minus) terminal to the Siemens S7 PLC terminals 1M and 2M. Then connect your 24 VDC power supply "+" terminal to ALL of your sensors and input switches. You will need to run many "+"wires, or run one "+"wire that jumps from sensor to sensor or switch-to-switch.
Also connect your new power supply "+" to the Siemens S7 PLC terminal L+, and connect power supply "-" to Siemens S7 PLC terminal M.
Because you will have two or more wires connecting to your power supply terminals, you will need a way to split 1 wire into many wires. You can use some "wire nuts" (wiring terminal connector devices) for that purpose.