Siemens Line Module to supply distributed Motor Modules

Kataeb

Member
Join Date
Jan 2007
Location
www.livelovelebanon.com
Posts
636
Can we use a central Active Line Module to supply with 540VDC power, Sinamics Double Motor Modules installed in other cabinets many meters away? Each cabinet containing five to ten modules.
Which protection should be used on the way? which cables?
 
I cant find max length in the manuals.
But Ive seen somewhere....seem to recall about 5 meters?
I know it can’t be very long
You find the specs?

Also make sure the wire insulation is at least 1000v
Don’t forget the dc link adapters and 24vdc adapters
 
Last edited:

Similar Topics

Hello Members: I am trying to control the Siemens S120 ActiveLine module with the Beckhoff EL6731 as Profibus master. I just want to switch the...
Replies
1
Views
3,136
A have a 12 axis S120 system where I have 6 axis on one CU and 6 on another. They all share the same Basic line module. The first CU though is...
Replies
28
Views
17,214
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
86
Hello, i can find the CPU when searching for it. But when I go Online i just get the icon for "Not compatible" everywhere. I get no additional...
Replies
4
Views
1,245
Hello guys, Im using a siemens with WINCC in a computer and need to import to tag´s data fom a specific row in a SCV file, i have a working...
Replies
15
Views
1,732
Back
Top Bottom