Siemens Micromaster MM440
rajendrad
May 2003
Pune, India
19
I am using Siemens Micromaster MM440 drive for one Application. I have to do the followings -
1. The Machine motor will have two motoring Torque limit settings, 150% and 50%. Motor torque setting is normally 150% except when the machine is approching its target position within 300 mm as sensed by Target position slowdown proximity switch.i.e means when its reaches to end position motor torque limit is set to 50%, if actual torque is beyond 50 % , then one digital output will be taken from drive and will send to PLC and then the locking device will be activated.
2,braking torque to set 100%
Which parameter I need to set to achieve above function.
I would copy the parameter set (0) using P819 to another set (1). Use P1503.1 to put the new torque setting. You will have to program an input to switch parameter sets (0) to (1). I don't remember how you switch the parameter sets.
Hello Everybody, Recently we changed the gearbox which has different ratio than the original one on a motor which is controlled by Micromaster...
1,903
Hello Experts I have to to make a backup of Siemens micromaster mm 440 with RS 485 to terminal 29&30. I use starter or drive monitor Do i need...
1,214
My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
2,982
fault A0501 (i.e current limit ) displaying whwn i replace siemens 420 drive with mm440. all parameters are crosschecked. please help to...
1,557
I have a Siemens Micromaster 440 (6SE6440-2UC25-5CA1) with encoder module (6SE6400-0EN00-0AA0) and Profibus module (6SE6400-1PB00-0AA0). I'm...
3,067