Siemens Modbus addressing
maico
Jun 2012
Belfast
27
Hi all,
Again another Modbus question, I have a s7 414-2 with a cp441 card I am sending and receiving data to deltav. Send block to deltav is db100 starting at Modbus address 40001(both AO & DO) receive block from deltav is db101 (bothAO & DO) starting at Modbus address 40513,
The problem is that I cant seem to receive any data on the Modbus address from deltav after 40553, up until this point all comms are fine, is this a config problem as if I am correct both systems should be able to address more than this!
Any help anyone!
Thx
I have experience with neither but experience with Modbus.
I find that the Modbus Standard provides a maximum limit on register transfer (125), but that implementations vary all over the place.
Some devices will not take more than a single register write, for example.
One device provided only 23 registers, attempts to get more than 23 failed. It wasn't documented, that's just the way it was.
So I have to ask, why do you think you are correct that the slave/server (DeltaV) should provide more than the 50 registers it is currently providing?
go with multiple read cycle with different data lengths say 32 word...
You will get the data...
I used a tool called CAS modbus scanner. Any modbus poller with an auto discover option will do. Launch it and it will simply map the data :)
When troubleshooting modbus problems you need a PC with modbus software that can act as a slave and as a master. There are a number of free ones on the net.
And of course a serial post with what ever interface you use RS232/422/485.
You want to communicate with delta v <-> PC and well as S7<->PC.
Then you can see what the problem is and what is sent.
You can also connect the PC so that you can read the traffic between S7 and delta V. This works best if you are using RS485 interface though as you only need one port on the PC to read both requests and replies.
117
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
284
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
914
Hi all, Happy belated turkey day! I have an ET200SP PLC with serial unit. We read out date from two energy meters using modbus RTU. We run a...
644
A customer site has 26 Nicotra Gebhardt EC PFP roof mounted ventilation fans. Control and monitoring is to be via Modbus RTU withing a Siemens...
559