Siemens Networking Help

kbradray

Member
Join Date
Jan 2006
Location
Columbia
Posts
175
I have a couple of 315 2PN/DP processors on the same subnet. I want to use the GET and PUT FBs to pull and push data from PLC to PLC. Can anyone provide information on how to create the network? I don't know if netpro is the solution or other ways.

Any help is appreciates.
 
I have a couple of 315 2PN/DP processors on the same subnet. I want to use the GET and PUT FBs to pull and push data from PLC to PLC. Can anyone provide information on how to create the network? I don't know if netpro is the solution or other ways.

Any help is appreciates.


Hello kbradray;
Yes, you have to use Netpro to establish a "connection" between the 2 CPUs before you program the SFC14 and SFC 15 (GET and PUT) functions. You will need the connection ID in order to program these.
Have a look at the following FAQ from Siemens, it discusses the requirements for Get/Put comms, and includes a downloadable program that you can use to prepare your own project:
http://support.automation.siemens.com/WW/view/en/18610307
Hope this helps,
Daniel Chartier
 

Similar Topics

Hi Every one I want to hookup the 10 numbers S7 300 PLC CPU on MPI Network . CPU,s are running on 10 different machines with 12 " HMI on each on...
Replies
5
Views
2,128
Ok then guys, I have a IM151-8 controlling a small stand alone filling/packaging line. When it was delivered it was set with the default...
Replies
5
Views
2,719
When i start the Siemens PLCSIM with some program uploaded, is it accesible from the network?For example if the hardware configuration have...
Replies
1
Views
4,057
Dear All, I have made a project with 2 plc's (CPU 414-2DP) and 3 PC stations connected with each other in profibus DP. All PC Stations use CP...
Replies
4
Views
3,634
Hi! to all If it`s possible that the siemens logo can communicate to a network PC. For example, I have a project with is a conveying line. The...
Replies
11
Views
11,132
Back
Top Bottom