Hello All,
IÂ’m starting a new project where the plc is connected throught LAN with external software which write some data on PLC db, obviously PLC is also connected with I/O devices and wincc.
The goal is to keep i/o device(and maybe also scada pc) outside of the main network while the PLC should be connected with that external software. The solution is to use PLC with 2 or more PN? There are other solutions?
Thanks in advance
Best Reagards
 
If you have something like a 1515-2, with two ethernet interfaces, this is easy. 1st interface goes to IO and HMI, 2nd interface goes to upper level network, to do whatever other thing you need.


If your PLC only has 1 interface, you can add a CP card to add another ethernet interface, or you could use something like an S615 to route to the other network (with firewall rules, etc, possibly NAT depending on the situation).
 

Similar Topics

Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
2
Views
72
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
480
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
214
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
372
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
186
Back
Top Bottom