SIEMENS PROFIBUS DP Networking
sherman4
Jun 2002
46
Hello all!
I have a Siemens S7-314C 2DP Controller and I would like to network this DP Master with 4 (four) Yaskawa Frequency Drives which are DP slave enabled.
How can I just add Drives which are not Siemens products to my Profibus Network using the S7 Simatic Manager Hardware Cofiguration?
I assume that because Profibus DP is a standard, I must be able to communicate a Siemens DP Master with any other DP Slave from any vendor.
Please confirm and indicate how to install the Drives GSD on the Hardware config for S7-314C 2DP
Thanks for the Help.
Double click Option after you have opened the hardware config , then you can Instal New GSD file , which will find itself in Additional Field Devices if your ctrl^K ,
don't forget to compile and save any changes . Take a not of the PIW and PQW for the device , then you can play with ladder and get it to go round and round
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
557
Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
788
I'm trying to figure out how to read the actual speed reference value from the move blocks, writing to a DB that is being sent to the VFD. For...
2,638
I have a piece of equipment with control split between two PLCs. A quantum 434, and a Siemens S7-300, communicating via profibus. I have a prosoft...
5,318
Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
17
4,811