Siemens s5 135u cpu problem

mouhab_ah

Member
Join Date
Jan 2014
Location
Egypt
Posts
20
Good morning
Please i need an advise,
I have a s5 135u cpu system , it is installed on printing machine.
Nowadays its stop about 10 times in 8 hours.
It give me qvs, and basp led and sometimes adf, and basp led.
I connect it to step5 and attached to you s screen shot of istack
Could you please told me which input module is damaged.

IMG_20210202_223550.jpg IMG_20210202_223347.jpg
 
QVZ is I/O timeout it sounds like you have a faulty card or bad connector to the card, I have had this mainly on analogue cards using direct access i.e. L PIWxxx or cyclic update of the I/O.
A major problem on some of these older racks is dirty connectors in the rack or dry joints, try removing & re-inserting the I/O cards this may clean the contacts enough. make sure it is powered down obviously.
Some years since used S5 but the address it stopped at is BLK-STOP at the top of the screen I believe there is a way to jump to this location, I think the address shown turns out to be 2 steps in front of the offending instruction so for example if the address xxx says XF, then two locations before is where it is probably accessing some I/O.
As there do not appear to be any data in the DB-ADD & accumulators it does sound like it's on I/O refresh this is happening i.e. before or after program scan.
 
Last edited:
Thanks for quick reply, i tried to clean the cards, but the result is the same, could you be more specific , because i'm not aware enough in step 5 .
The vek-address that it gave me is F268 , is that meaning any thing , and for your note about blk-stp 00E0 how i can find it .
 
it's best if you give all the part numbers of all modules in your rack, and any remote racks (S5 expansion racks and/or ET200/Profibus racks). It's possible I24 is indirectly addressed.

And the STEP 5 program, if possible.

I will collect the information, about the part number , but can you send me your mail to send the program to you.
 

Similar Topics

I have an Siemens S5 135 system. The CPU 6ES5 928-3UB12 Will not go into run mode even after a MASTER RESET or AN OVERALL RESET using a...
Replies
2
Views
2,867
i have a siemens 135u plc cpu which is in stop mode. the number of the processor is 6es59223ua11. i dont have a programmer so i need help on how...
Replies
8
Views
6,236
hello miss/mr We have a control system that works with plc S5-135U. two cpu (p/n:6ES5 921 & 922)of plc have ram card. The problme is...
Replies
2
Views
1,582
Dear friends I face a problem with my Refinery PLC unit SIEMENS S5 135U -3UA11 is now not functioning The problem start after a CPU's fan fault.I...
Replies
5
Views
8,427
I have 135 U siemens make PLC and recently we have trouble of flickering of BVQ red led intermitently. Pl. tell me the reasons for troubleshooting...
Replies
6
Views
4,962
Back
Top Bottom