Siemens S7-417H redundant cpu

Andy32821

Member
Join Date
Aug 2003
Location
Orlando
Posts
5
I have two siemens S7-417H cpu’s that run as a redundant pair. On the project tree menu both cpu’s are shown but only one S-7 program shows under one of the cpu’s. I have made programming changes to this S7-Program.

My questions:

Do I need to somehow save this revised program to the backup cpu?

If so, how do I do it?


The cpu’s have a memory card in each cpu.

How do I save the revised program to these cards?
Thanks, Andy
 
Hi, there:

Depend on what kind of memeory card you use. If it is a RAM memory, you can simply download your revised program into CPU because CPU's RAM and your RAM card are simply merged together.

If you use a Flash memory card and your CPU memory is big enough say 1 MB, you can simply download your revised program, and then copy from RAM to ROM.

Hope it can help you.

Best regards,

Jason
 

Similar Topics

G
I am working on a project where there is an S7-417H PLC with ET200 I/O on redundant profibus. One of my I/O drops has 1 pair of existing fibers...
Replies
5
Views
7,016
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
Replies
10
Views
184
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
83
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
9
Views
172
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
5
Views
205
Back
Top Bottom