Siemens S7 Modbus Switching over
macs_plc
Jan 2008
Nagercoil
120
I am using Modbus protocol to exchange data between Siemens S7 and Foxboro DCS using CP341 (S7-300) redundant
communication looks healthy and the data transfer is fine, but the issue is Master Slave switch over happens every 1 minute, for that switch over time we are loosing the live data in the HMI of DCS....I don't know wat is wrong in this...
Suggestions please....let me know if you want anything specific....
Regards
Macs
Hi....Both the CPUs and CPs are redundant...
For making CPs redundant some codes have been written with 4 different DBs (2 DBs for Mod_Slave A and 2 DBs for Mod_Slave B) and it moves the data to each other by two function and it is executed by OB1.
The code maker has resigned the job and gone some where......this issue is here for past 7 months. no one is ready to take this....
Regards Macs....
Hmm, a one of a kind solution...
Is the Foxboro the Modbus master and the 2 x 2 CP-cards slaves?
With identical node number? The master does the switchover?
How is it intended to work? You don't have a flowchart / connection diagram / HW configuration to show us?
Kalle
thank you...will have a look at it....in the meantime...i will try to send you the hardware configuration / flow chart...
124
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
290
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
961
Hi all, Happy belated turkey day! I have an ET200SP PLC with serial unit. We read out date from two energy meters using modbus RTU. We run a...
647
A customer site has 26 Nicotra Gebhardt EC PFP roof mounted ventilation fans. Control and monitoring is to be via Modbus RTU withing a Siemens...
560