Siemens S7 PID Reset input format
Andy32821
Aug 2003
Orlando
I am to writing a floating point number for PID “reset time” from a SCADA HMI to a data block register in a S7-400 processor simatic PLC. Contrary to some published data I cannot get the PID block to read milliseconds. The PID block seems to insist that the reset and rate times be in siemens’ “time format” data type before the PID block will read them.
Can I force the PID block to accept milliseconds?
Is there a math block that will convert decimal into time format?
Thanks, Andy
S5-Timer-format for preset-variable
15.............0 = timer preset
bits 15,14,13,12 are the time-base bits
xx00=timebase 10 ms
xx01=timebase 100 ms
xx10=timebase 1 second
xx11=timebase 10 second
bits 0 to 11 are for preset in BCD format, so max is 999
In 'Program elements/ Standard Library/ S5-S7 Converting Blocks'
have FC62 for Float to Fix Converting.
Also you need Fix to BCD convert-command.
You must check value and 'time-base' and try convert that to
S5-Timer-format
Are there tools in Scada for this , scripting ?
Thanks for the reply. I think I had better keep this part in the PLC. I was hoping siemens had something a little more elegant since this must be a common tast to programers. Maybe I will try the S7 scripting and see if it"s code is less messy than the ladder blocks.
Hello all, A group I am involved with is just completing converting a Siemens APACS control system over to an RSLogix PLC. The subject came up of...
1,219
Hi, Have problem with getting PID to work. Have been using 4x different programmers on siemens, not one could make PID to work as I want. Problem...
1,758
Urgent, Commissioning deadline. I am using CONT_C in a function block. I call the FB in a Cyclic Program (OB32). when the PID is in manual I...
3,329
I'm trying to program the PID function of a G120 drive using Starter. The PID output looks good but the "limitation active" LED is always on...
1,661
Can any one help me regarding how to give set point via field bus for control yasakawa a1000 drive while it is running on PID operation. Also i...
1,484