There is code in the siemens PLC to control the pressure of 1 giant spinning roll against another giant spinning roll using 2 hydraulic cylinders. The hydraulic cylinders are actuated using 2 24vdc PWM servo valves. These 2 valves are controlled using an amplifier module that takes 2 4-20ma signals from the PLC and converts it to PWM signal for the valves.
I am trying to understand the code for converting a pressure setpoint as set through an HMI to a 4-20ma output to the valve amplifier.
I attached some screen shots of 2 networks that I don't understand what is happening.
I found a PDF of STL's http://www.plcdev.com/files/plcdev/STL-cheat-sheet-by-alphabet.pdf and tried figuring it out
How I understand Network 22.
  • Load DB11.DBW176 (Left Pressure Setpoint, as set through HMI)to ACC2???
  • Convert value in ACC2 from Integer to Double Integer
  • Convert value in ACC2 from Double Integer to Floating Point
  • Load 1 to ACC1
  • Divide ACC2 by ACC1 (so divide setpoint by 1)
  • Transfer result to DB11.DBD140
  • Load DB11.DBD140
  • Transfer to Pressure Left (In german its Solldruck_Links_Steuer)
  • Load Pressure Left to ACC2
  • Load 8.00000 to ACC1
  • Divide ACC2 by ACC1 (so divide Pressure Left by 8.0000000)
  • Load 2.76480000 to ACC1
  • Multiply ACC1 by ACC2 (2.76480000 by previous result)
  • Round result
  • Transfer result to Pressure Left Scaled
  • Load Pressure Left Scaled to ACC2
  • Transfer Pressure Left Scaled to Output Pressure Roll Left
I noticed the pictures are too big to attached. I'll host them from photobucket and post the links.
Until I get the pictures hosted these are the statement letters
  • L
  • ITD
  • DTR
  • L
  • /R
  • T
  • L
  • T
  • L
  • L
  • /R
  • L
  • *R
  • RND
  • T
  • L
  • T
I was trying to communicate between Siemens ET200S IM-151-8 PN/DP CPU to Rockwell Allen Bradley L73 through Hilscher Gateway NT100-RE-EN. Using...
113
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
654
Good morning all, I've got a customer in a bind. They, like many, got confused about Allen Bradley's EtherNet/IP protocol and assumed it was...
2,650
hi guys I have allen Bradley software on a laptop , and would like to but siemens tia portal and classic on the same laptop ? is there still...
1,363
Hello Experts, I hope everyone is safe and healthy!! Below mentioned Siemens code is in STL i have to write it in Structure text in Allen...
1,652