Hi all,
It's been a while since I've done someting with safety.
I have a Safety PLC with failsafe remote IO via ET200M.
I made the hardware and configured o1001 and o1002 where needed and deactivated the not necessary channels.
When Compiling the hardware I was expecting that the Safety DB's would be generated automatically, but that isn't the case.
Any ideas what I forget here ?
Thanks in advance,
Kind regards,
C
Found
Found, damn :)
Protection, add password and then you can checkmark: CPU Contains Safety
Regards,
C
Yes, but is for in the safey check, you can see this in a VAT table. Just add all off the address of the module in a VAT and behold the disco lights.
As he said, this is where the Profisafe data is processed. 1 Byte of inputs ends up taking something like 6 bytes in and 5 bytes out due to all the CRC checks, profisafe addresses, diagnostics, etc. Don't worry about all that extra stuff.
If you right click on the card, there should be an option to do something like "edit symbols". That tells you which IO points are actually relevant.
Hi! Doing a lab project with two 1214FC. Got a warning about reintegration of modules wasn´t configured and tried to do that. Found the two...
805
I am working on a program that was developed in 2015 for an S7-300 safety PLC. The new copy of this machine uses an S7-1500 safety plc. We were...
1,902
Our system has S7 1516 F CPU. We have doors that have contactless safety doorcontact that is cat 4 ple rated. The sensor provides us with two...
3,006
I have a project I am working on and having issues with the analog, I am using below. 6ES7511-1UK01-0AB0 (Safety CPU) 6ES7523-1BL00-0AA0...
1,484
Hi all! Just got some comments from a client regarding a safety block we made. They want us to replace JMP statements with other logic. They...
2,266