Siemens Sinamics G120C fixed speed setpoint
mulderm
Jun 2003
Netherlands
298
Hello,
I use a Siemens Sinamics G120C inverter in combination with a S7-1200 cpu.
I use the Main Setpoint with the Providrive option and send 1810 rpm to the inverter.
Now I use r722.3 digital input to select a fixed speed of 300 rpm.
But when I activated this input the totaly speed will be 2110 rpm, the fixed speed will be added.
See attachment.
I can calculated to get 300 rpm but when the main setpoint changes I get another speed then 300 rpm.
So independent of the main setpoint via Profidrive (I must use this for other situations) when I activated r722.3 always the drive must be 300 rpm.
Who can help me to fix this?
Thanx, mulderm
So, from the diagram, the "fixed" setpoint is added to the main setpoint. If you add a negative number do you get 300 rpm? If so, can you do logic in the PLC to get the fixed setpoint. (Main SP - 300) * -1 = Addition SP
Hello Ken,
Yes that is right.
I add a negative number on it and then I get 300 rpm.
But when the main setpoint changed I get no 300 rpm.
I think I can't send the fixed calculation to the inverter, it is adjusting in the settings.
Greetings,
mulderm
They are easy to use
Post your specific questions
Also
You can map r722 io back to the plc too
And do the logic in the plc …
If you find writing it the pic better for you
JRW,
I am on the good way, it works with the free function blocks.
See attachment.
Goal is to start a motor with the profidrive setpoint and after a time I will
give the motor a slow speed and then after a setting time the motor must be stopped.
Then after a few seconds the motor start again.
Problem is that I use OFF1 to stop the motor, but I want to give a 0 rpm in the settings or free function blocks but I don't know how to do that.
Now the inverter stops every time and also the fan, I don't want that.
I will use a setpoint of 0 rpm to put this without using in the plc-program
Can you help me with the blocks?
Thnx,
mulderm
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
101
I have G120 with Firmware version V4.7.13. In the TIA project, I have version V4.7.10. I would like to install new firmware HSP in my project. I...
1,865
Hi , A little off topic , hope you don't mind I have a Siemens Sinamics V20 Inverter On a 0 - 10 v analogue input as a speed reference...
1,081
Good day Wanting to learn about servos, I bought from Ebay, a USED Siemens Sinamics S210 servo drive with the 1FK2130-2AG00-2SA0 motor. The unit...
1,514
Hi All I have done the commissioning wizzard on the drive with Tia portal V15.1 and all good , but once i go to acceptance test and click on STO...
2,205