siemens sitrans P ped sep differential pressure transmitter

shkoko2000

Member
Join Date
May 2011
Location
cairo
Posts
296
i have siemens sitrans P ped sep differential pressure transmitter used for measuring flow is it have square root built in or i must built equation at plc and how i know that from manual
 
>how i know that from manual

Siemens manual are pdf format. Open the manual in a pdf reader and search the manual for the word square, then see if any 'hits' apply to a square root function.

Only DP transmitters will have a square root function.

Can you provide a link to the "siemens sitrans P ped sep" spec sheet or manual?

The term "ped sep" appears on Siemens stainless rivet tags, but no one knows what it means.
 
As Osmanmom says PED and SEP are directives. We use PED for pressure vessel design.

I think you can either activate or deactivate the square root function in the DP transmitter. Probably using HART.
 

Similar Topics

hello Can you help me to find or explain me, how can i drive a vacuum system of -0.38 to 0.42 psi, i want to manage it from transmission SITRANS...
Replies
4
Views
1,627
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
8
Views
42
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
308
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
163
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
313
Back