silo problems
tczjr5
Mar 2009
illinois
when switch C is on stoping the box just past the level sensor and moving the switch to a the soleniod vavle opens and fills the factory what iam i missing???
I would break the tasks down into small pieces. First, transport the box to the filling point.
I would use a "Set" command (Not sure what it is in AB!)to say transport on. When the box arrives in position a "Fill" flag is set (And the transport flag reset). The fill flag opens the fill valve and looks for the level probe. The full level probe "Sets" a box full flag and resets the fill flag.
The box full flag starts the transport to discharge the full box - and so on.
I hope this is what you were after?
PS. You could build on this by limiting the time the fill valve is open - set an alarm that says the box has got a hole in it!!! Or the sensor is faulty etc...
Tczjr5,
You have the logic for your Conveyor Motor Output O:2/0 very close, but not quite correct if using the 3-position Selector Switch. Also, a "Full" indicator should never be compromised. If a box is full, the indicator light should show that, regardless of the Selector Switch position. Any other way makes a liar out of the indicator, and lying indicators just do not work in the real world.
Here is one way to do this program.
Tczjr5,
The Silo Simulator program that I posted above needs one more rung to make it fill the box completely (I:1/4 indicates full every time) without ever having a spill. In the materials handling industry it is called a "dribble mode" for the solenoid valve. After reaching the Nearly Full level, the Dribble Mode takes over and pulses the solenoid slowly until the box is Full. Add one internal relay bit to control the dribble mode.
seltor A lets the box stop and fill and once full the conveyor starts too bring the next box THe B switch stop and fills and has to be restarted...
1,555
Customer does not want any silo penetrations. Hates level sensors on top of silos. No capacitance sensors either. Would be great if it had...
1,517
I am looking for a way to determine level in a silo. The material is called Perilite which has a very light density. Bulk density could be...
2,762
Hi, i have a problem with measuring level in silo using siemens S7-1200. On top of the silo there is an 0-10V radar level sensor, it works...
3,705
I am working with plc5. I am using the CPT function but getting errors. The level of the silo is inputed at F51:031. The silo cuft is 3393 with...
1,610