SIMATIC 545 error
jayare12
Dec 2010
oregon
20
I am currently trying to convert a cti2500 program to a 545-1106 and everytime I transfer online I get a failed to write I/O configuration. Address out of range(other than ladder logic). What does this mean? I am using 505 workshop as my programming software and I am connected with a serial cable
The CTI 2500 is larger and supports higher I/O addressing. I know the 545 limit for analogs is 1024 so if you have a WX1025 or higher you get this error, there are limits on the discretes also , but I do not recall the exact number. The software usually points to the first network with this issue. Can you post the exact error message?
If it is a 'full blown' 545 it will support 1k of word I/O but 2k of discrete I/O; so this means that the first 1k can be mixed discrete and word, but the 2nd K of I/O can only be discrete points. The 545 'lite' only supports 1k period (mixed word / discrete).
Tom
I got it it was that someone had added an analog output card to one of the bases and started the I/O at 1041. Also as for the acctual error message it was "Failed to write I/O configuration. Address out of range(other than ladder logic).
What software and cable are used to program a Simatic 545? We have 3 on winders and need to make a small program change for a new product line...
1,825
Hi - I am looking for contractors in the western US experienced in TI / Simatic 545 programming. This would be small project type work -...
1,922
Hi: I have a CTI-2552-A card which is "isolated rtd input". The card replaced a 505-7038. The temperature values are reading too high, on all...
1,311
I had a problem on a plc I am not versed on. a 545 could not get it into run and could not connect... we replaced the card dumped the program in...
3,111
Hi, I have received from a client a SIMATIC 545. When I put power to it, CPU Good and RUN lights are ON. I can connect to it and see ladder...
3,024