Simatic ET 200S CPU

jillgeorge18

Member
Join Date
Feb 2016
Location
Cochin
Posts
26
Hello to All,May I know the difference between local io and distributed io ?and what's the function of fail safe modules in ET200S?? and If I have a S7 300 CPU and can I use ET200S as a slave device through Profinet??:mad::mad:
 
The difference between distributed and traditional I/O is it the name, its distributed. You would use distributed I/O when you want more than 1 point where are all the wires are going to.
Traditional I/O has all of the wires going to 1 point, the MCC (main control cabinet). With distributed I/O you would spread this by having additional smaller cabinets with its own I/O.

The function of failsave I/O in a ET200s is to use it in concjuction with a saftey plc. With a safety cpu and saftey IO you can wire E-Stops directly to the remote I/O stations.

Yes you can use a ET200S as a remote I/O station, you could use a IM151-3pn for this. If you want safety in this station you need a HF (high feature) version of this interface module
 

Similar Topics

Hello to All,May I know what are the main advantages of Simatic ET 200S with respect to other S7 CPUs????I tried to get from internet but some...
Replies
5
Views
2,063
Hello. I'm trying to comunicate to Siemens SIMATIC ET 200S IM 151-8 PN F-CPU using CitectNexa 6.1 via Ethernet. I don't know wich Citect driver...
Replies
1
Views
1,723
Hi guys, I think, you know this issue... the last power module at the ET200S rack (sometimes) indicates system fault (SF diode) but everything is...
Replies
0
Views
3,180
Sorry for my mistake... how to delete this thread?
Replies
0
Views
2,546
We are facing intermittent issue with emergency stop and line stop. Line stop triggering with alarm of line stop push button activated at one...
Replies
10
Views
207
Back
Top Bottom