SIMATIC: Problems writing a value
May 2009
Halmstad
41
Hey all!
I've been developing a function block, and at the end of this function block I want to write error code to an output variable, #RET. If there were no error, I want to write the value w#16#0, if there were an error, I want the error code to be returned. Here is the code:
Code:
err:  NOP   0
      L     #iReturn
      L     W#16#8000                   // Make sure the error bit is set
      OW
      T     #RET                        // Write the error information to the RET variable
      SET
      SAVE
      JU    exit
done: NOP   0
      L     0                           // Make sure the RET variable indicates no error has occured
      T     #RET
      SET
      SAVE
exit: NOP   0
This only works halfway. If I have an error, the error code is written to #RET and there's nothing strange about that. But when there is no error, the execution jumps to done (and the code between err and done is never executed), but still the previous error code sticks. When getting another error code, the #RET is changed immediately, but as soon as I clear every error, nothing happens.
I managed to get the things working by changing the code to this:
Code:
err:  NOP   0
      L     #iReturn
      OW
      SET
      SAVE
      JU    exit
done: NOP   0
      L     P##RET                      // Make sure the RET variable indicates no error has occured
      LAR1
      L     0
      T     W [AR1,P#0.0]
      SET
      SAVE
exit: NOP   0
Where the only change is after the done label.
Does anyone have an explination why it didn't work with the first code?
Its seems like compiler has been buggy or sumthing. It should work as you want, have no idea, if you do not tamper with AR2 before executing jump.
Well, I do tamper with AR2, but a bit further up in the code. Could this affect anything?
Here comes the code that jumps to done
Code:
      LAR1  P##pSrc
      L     W#16#1002
      T     W [AR1,P#0.0]
      L     #wBPSize
      T     W [AR1,P#2.0]
      L     DINO
      T     W [AR1,P#4.0]
      L     P##abSendBuffer
      T     D [AR1,P#6.0]
      CALL  "DPWR_DAT"                  // Write the send buffer to outputs
       LADDR  :=#wLADDROut
       RECORD :=#pSrc
       RET_VAL:=#iReturn
      L     #iReturn
      L     0
      ==I
      JNB   err
      JU    done
In the 300 CPUs when you execute a conditional jump the state of the RLO Bit is carried over after the jump is executed (this doesn't happen in the 400 CPUs). This means that when you arrive at the error check, in your case, you have the RLO Bit already set. The OR command then looks at the result of the immediate comparison and ORs it with the current state of the RLO, since this is TRUE then the result of the OR is TRUe.
Either invert your error query and test for no error and change your Jump to JCN (or whatever the English mnemonic is, I don't have a PC with Step7 available at the moment), or alternatively, as the first command in the error check issue a CLR instruction to reset the RLO Bit.
If you make a habit of checking things this way, then it might be a good idea to get into the habit of always CLRing the RLO in code you jump to conditionally.
This problem doesn't have anything to do with AR2.
I mean the "OW" command which you use to strip out the error Bit in the third line after the "err" label. I can't check it, but I assume that the OW command operates the same way as the O command for ORing two Bools and ORs the result with the state of the RLO Bit.
While I try to find my copy of Berger, try inserting a CLR command as the first instruction after your
err: NOP 0
label. I reckon that will solve your problem - at least it will if I'm correct! ;)
I think you misunderstood my question/problem.
The error code is reported correctly when jumping to the "err" label. the OW ORs ACCU1 and ACCU2, in this case making sure bit 15 is set, as I'm ORing w#16#8000. The OW instruction is executed as I want.
The thing that confuses me is why
Code:
L 0
T #RET
doesn't work, when
Code:
L P##RET
LAR1
L 0
T W[AR1, P0.0]
does?
Anyways, I tried CLR after the err: NOP 0 row, but it didn't help. :(
Hi, I would like to know if one can use a 6ES5721-0CD20 instead of 6ES5721-0CE00. If anybody has information or datasheets for 6ES5721 - 0XXX0...
1,771
Evening all, I'm currently trying to get my head round the siemens s7 and the simatic hmi range and have hit a problem with a simatic hmi. (why...
6,052
hi to all members here, i have visit a damage ready system with S7-300 plc units for repair hw and s/w :hmmm: there is a strange prob , when i try...
3,016
I have a Simatic S5 communicating with a Yokogawa DCS through RS232 and ACM11. The network, communication module are cool and the S5 as well as...
4,064
Hello I have compiled a simple program in Protool and when I try to transfer it to the OP C7-635 it starts transmiting and then stops at this...
10,319