if an i/p is calibrated for 10-50ma input equals 6-50psi out. what is the out at 25ma?
What is the formula to get this?
Thanks in advance,
Jason
22.5 PSI
(( Current Value - 10 ma) / ( Max Current Value - Min Current Value)) x ( Max Output - Min Output) + 6 = Output
(( 25ma - 10ma) / ( 50ma - 10ma)) x ( 50 - 6) + 6 = Output
(( 15ma) / (40ma)) x (44psi)) + 6psi = output
(.375 x 44) + 6 = 22.5
tutu types faster then I do.
See attached for a handy tool
newguru said:
thanks, for the quick reply. Mickey the scaling chart is exactly what I needed.
Your welcome. The chart is not mine, I dowloaded it from this site. I'm not sure who gets the credit. Maybe he/she will check in and take a bow.
That's me. Check the Excel file properties.
I use it for calibration checking charts when I have the techs install instruments. What is handy is the PLC counts. If you are looking at the raw value in a register just check the chart. Or don't have a MA meter but have a voltmeter to check the loop and it has a 250 ohm resistor check volts in the chart. I carry a pencil type VOM and a 250 ohm resistor for quick checks. I also have a version of the Excel chart running on my pocket PC.
hey Guys, I want to take my five counters, add them and multiple by 10, I got it to work, but WAY to many lines. Any suggestions...
1,799
Hi everyone, I am having a little problem verifying some math results being done in DL06. Doing simple math in DL06 suppose to be relatively...
4,747
Hello, I´m having a problem trying to program in Ladder. An output should be trigged by two possible contacts. Take a look on the printscreen...
180
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
201
Hi all, Writng a FB in ST on Beckhoff TC for a pulser which turns on and off on a cycle, is paused by turning bControlInput to FALSE, but resumes...
308