Simple question regarding the CLick PLC
Here is a link to the manual for the drive series in your link.
http://www.automationdirect.com/static/specs/gs1drives.pdf
See page e13-19 for a typical wiring diagram for the drive.
You will need the Click manual for the wiring diagram for the PLC end. You will also need to select current or voltage for both devices, keeping them the same. I personally prefer current but both will work. Each have their limitations.
Your original link didn't work very well. I added the ) manually at the end. It just doesn't copy and paste correctly here for some reason.
Here is a link for the PLC manual.
http://www.automationdirect.com/static/specs/c002dd1d.pdf
The typical voltage and current wiring is illustrated on page e1-49.
Please notice the difference in voltage range of the output of the PLC (1 to 5) verses the input range (0 to 10) of the drive. That is why I prefer the current output and input. They can be matched (4 to 20ma) in hardware to simplify the setup.
Hi, I'm pretty new at this whole PLC thing. If you have a branch in the input section of a rung what does that mean? Is the branch true if every...
4,263
When one refers to linearization of an analog input does it mean converting the signal into a value that is useful? How exactly is this done? Am...
10,628
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
169
Hi all, Writng a FB in ST on Beckhoff TC for a pulser which turns on and off on a cycle, is paused by turning bControlInput to FALSE, but resumes...
255
Hi all, I have a simple question that I have overcomplicated and gotten stuck on. I have a variable, we can call it "light" that I need to stay...
317