Single Ended vs Differential
bodoo23
Jan 2018
Athens
57
I actually don't understand which device determines whether the wiring will be single ended vs differential.
being single ended or differential is a property of transmitter or input module (or both) ?
Briefly, I'd like to ask how can I decide which wiring method to use ?
These pictures might help. As far as which wiring methods to use, it seems to depend on if your signals will be in an electrically noisy area.
Edit: These are for Allen-Bradley PLC cards, but the concept should translate.
As mentioned, differential gives you better noise reduction. With single ended, all the instruments share a common. One noisy signal can make all signals noisy. The single ended/differential is determined by how the input module is configured, and how it is wired. A lot of budget mined folks always use single ended. If possible I steer my clients, to differential. Less potential for issues.
Hello, I have a 1756-IF16 configured for single-ended current inputs. I plan to add (4) 4-wire density transmitters. The operating manual for...
2,477
Hello, I am attempting to wire instrumentation to an AB IF16 analog input card. In examining the documentation for the card, I've come to know...
7,238
Hi all, I have a PLC5 rack that is actually full(No place for an aditionnal card). The rack has a couple of spare inputs on 1771-IFE cards and I...
3,718
Ok, here's what's going on with me. As silly as this might sound, I just have a hard time fully understand the difference between Sngle ended and...
6,042
We are attempting to interface an AD H0-CTRIO counter to a system which has a differential (RS485 driver) quadrature encoder signal. We need to...
8,694